Wiring HCC80R to a motorised valve as well as a pump

Posted: Mon Jan 16, 2023 3:27 pm
by Rwshack
Hello

First time poster so please be kind!

I have a 4 zone UFH setup with a Heatmiser UH8 controlling the zones, the rest of the house I use Evohome with HR92 valves on the radiators, so want to change the UFH control to HCC80R, but I'm a little confused by the wiring.

There is a motorised valve as well as the pump which is controlled by the UH8, so do I simply wire both of these into the pump live in the HCC80R, or use a BDR91 to control the valve and wire the pump to the HCC80R?

Thanks in advance.

Re: Wiring HCC80R to a motorised valve as well as a pump

Posted: Mon Jan 30, 2023 9:10 am
by Richard
You just wire both items to the switched live on the HCC80R (hence there are two terminals on the switched live).