Honeywell Evohome Viessmann Vitodens 222-F -- help
Posted: Sat Dec 03, 2022 1:47 pm
hey all,
I had an old boiler that was setup with my evohome system, 12 zones in my house, with controls on each radiator - all worked well.
Honeywell THR99C3112 Evotouch controller
HR92 Radiator controllers
Relay box
I needed to change the boiler however, so had a new Viessmann Vitodens 222-F B2TF 32KW installed.
https://www.viessmann.co.uk/en/products ... 222-f.html
Am i correct in thinking this IS opentherm? so it should work with my honeywell setup?
i do see it mentioned here: https://viessmanndirect.co.uk/files//16 ... ctions.PDF
Currently they dont all talk and so its a nightmare trying to set the boiler to a temp and then have it work with the rads, as the outdoor temp and the whole heating curve things play havoc with it all!
im getting various errors, such as Viessman dhw heating flow rate not reached and high-limit safety cut out
I had an old boiler that was setup with my evohome system, 12 zones in my house, with controls on each radiator - all worked well.
Honeywell THR99C3112 Evotouch controller
HR92 Radiator controllers
Relay box
I needed to change the boiler however, so had a new Viessmann Vitodens 222-F B2TF 32KW installed.
https://www.viessmann.co.uk/en/products ... 222-f.html
Am i correct in thinking this IS opentherm? so it should work with my honeywell setup?
i do see it mentioned here: https://viessmanndirect.co.uk/files//16 ... ctions.PDF
Currently they dont all talk and so its a nightmare trying to set the boiler to a temp and then have it work with the rads, as the outdoor temp and the whole heating curve things play havoc with it all!
im getting various errors, such as Viessman dhw heating flow rate not reached and high-limit safety cut out