intermittent delay in controller registering cylinder temp

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
lonach
Posts: 2
Joined: Tue Jul 31, 2018 10:26 am

intermittent delay in controller registering cylinder temp

Post by lonach »

Hi. My system has worked fine for a few years now. Recently, I have noticed the cylinder going overtemperature. The controller says the temperature is fine. It then displays the correct temperature and behaves properly. It appears that there is occasionally a delay in the controller having the correct temperature. How often should the cs92 transmit the temperature data?
It works fine most of the time, but obviously I would like to prevent the boiler pushing the water temperature up too high.
Anyone come across this?
Thanks
Graham
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: intermittent delay in controller registering cylinder te

Post by Richard »

CS92A when located and fitted correctly will transmit data based on temperature change and as temperature gets closer to setpoint transmission rate increases. When was the last time the batteries were change in it?
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
lonach
Posts: 2
Joined: Tue Jul 31, 2018 10:26 am

Re: intermittent delay in controller registering cylinder te

Post by lonach »

Hi ... thanks for the reply. They are actually brand new batteries ... but the resideo chap said they have to be high quality batteries. I have now changed them from amazon to duracell and have not hat a repeat event. (previously it was at least two a day). That might be it! Fingers crossed.