This is the diagram of the wiring of my boiler when the circuit is closed and it is heating the water in the hot water cylinder.

Image

In my boiler, I have three contacts Tc, TB1, and TB2 as shown in the picture.

Which is supposed to be the correct wiring in the BDR91?

Since according to the Honeywell diagrams, the wiring in the BDR91 is made connecting wires only to A and B leaving C not connected and used when the circuit is closed. But what about when I have three wires?

Re: Proper wiring for the heating of the hot water

Posted: Sat Nov 06, 2021 8:30 pm
by mazzy89
The connection I would make would be the following

BDR91 | Boiler
A Tc
B TB1
C TB2

In this way when the circuit is closed A and B are closed and the BDR91 is active. otherwise the circuit is opened

Re: Proper wiring for the heating of the hot water

Posted: Mon Nov 08, 2021 10:10 am
by Richard
Yes, if you have a Motor Open / Motor Closed zone valve, you would need to use the C contact.

Re: Proper wiring for the heating of the hot water

Posted: Mon Nov 08, 2021 6:21 pm
by mazzy89
Thanks a lot. it worked.