Cs92 & BDR issue

Post by Stusimpson »

Hi I’ve had a perfectly working Evohome system for 3 years, no issues.

The other day the water was cold so I went to the controller and saw a small red triangle on the hot water display with no temperature displayed . Faults suggested a Hot water sensor and Hot water valve error.

On going up to the loft , all 3 BDR91’s (upstairs,downstairs and hot water) had a solid red light on. I changed the CS92 batteries, all the lights seemed to go off, the upstairs/downstairs work fine from the app and controller, boiler works fine and the valves move.

Faults say restored and I can call the hot water by pressing the BDR91 but not from app or controller, they do nothing. If I press the CS92 for 5 secs it flashes 5 reds and a green, but that’s it.I can’t seem to get the BDR91 for the hot water to be activated via anything other than the button.

Any help greatly appreciated !

Cheers Stu
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Cs92 & BDR issue

Post by Richard »

It was probably the CS92 screening the system. At the point you changed the batteries the system would have settled down.