Ideal Logic Heat & Logic System Boilers & OpenTherm Bridge
Posted: Fri Apr 05, 2019 9:24 am
OK, so again Ideal and Resideo (Honeywell Home) seem to argue over the correct way to install the evohome OpenTherm Bridge on an Ideal boiler...
So, the best document I can find is this one from Ideal (as their Boiler Installation Guide details on the OpenTherm connection is useless) - https://idealboilers.com/uploads/docume ... _Guide.pdf
In this guide for their own OpenTherm thermostat it states...
"*Where the Ideal Touch kit is being fitted to an existing installation (S or Y plan), the wire
connecting any SL IN on the boiler requires disconnecting and making safe. A link wire
should then be connected into the SL1 L-IN connection at the boiler*.
For further details refer to the boiler installation and sevicing instructions.
*Logic Heat H, Logic System S, Vogue Gen2 System"
To confirm, you should have no other wires attached to the Weather Compensation terminals or the 230v SL2 and your wiring should look like this below...
The 230v side should look like this... The OpenTherm terminal should look like this (link wire removed and then two wires attached to the OpenTherm terminal and then the same two wires attached to the OpenTherm Bridge)... Once you power the boiler back on, the OpenTherm Bridge should 'flash' either a red light OR a green light every 10 seconds (depending if the OpenTherm Bridge is pre-bound or not).
If you have any questions, please ask.
So, the best document I can find is this one from Ideal (as their Boiler Installation Guide details on the OpenTherm connection is useless) - https://idealboilers.com/uploads/docume ... _Guide.pdf
In this guide for their own OpenTherm thermostat it states...
"*Where the Ideal Touch kit is being fitted to an existing installation (S or Y plan), the wire
connecting any SL IN on the boiler requires disconnecting and making safe. A link wire
should then be connected into the SL1 L-IN connection at the boiler*.
For further details refer to the boiler installation and sevicing instructions.
*Logic Heat H, Logic System S, Vogue Gen2 System"
To confirm, you should have no other wires attached to the Weather Compensation terminals or the 230v SL2 and your wiring should look like this below...
The 230v side should look like this... The OpenTherm terminal should look like this (link wire removed and then two wires attached to the OpenTherm terminal and then the same two wires attached to the OpenTherm Bridge)... Once you power the boiler back on, the OpenTherm Bridge should 'flash' either a red light OR a green light every 10 seconds (depending if the OpenTherm Bridge is pre-bound or not).
If you have any questions, please ask.