Automatically heating hot water cylinder when temp is low

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
MrM
Posts: 1
Joined: Thu Feb 14, 2019 3:05 pm

Automatically heating hot water cylinder when temp is low

Post by MrM »

Hi All,

I am looking for some advice as the title really. Is it possible to configure Evohome to automatically heat the hot water cylinder when the temperature reaches a certain low level?

Thanks
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Automatically heating hot water cylinder when temp is lo

Post by Richard »

evohome has the capability to be programmed with an 'differential' before reheat of the cylinder commences, however the maximum this can be set to is 10 deg C. So a 60 deg C set temp would have to fall below 50 deg C before it would come back on.

I hope that helps.
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
kevinsmart
Posts: 3
Joined: Tue Nov 21, 2017 9:00 pm

Re: Automatically heating hot water cylinder when temp is lo

Post by kevinsmart »

Evohome will automatically reheat the DHW if the temperature drops below a low threshold, similar to frost protection.

During the winter I’ve seen it kick-in, even when scheduled Off, heating from a displayed temperature of around 14C to 25C.
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Automatically heating hot water cylinder when temp is lo

Post by Richard »

kevinsmart wrote:Evohome will automatically reheat the DHW if the temperature drops below a low threshold, similar to frost protection.

During the winter I’ve seen it kick-in, even when scheduled Off, heating from a displayed temperature of around 14C to 25C.
evohome will only reheat a cylinder when it is scheduled to do so. The only time it would ever heat the cylinder without schedule, is if it thought the cylinder was at risk of freezing.
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
BillM
Posts: 2
Joined: Sun Mar 17, 2019 10:55 am

Re: Automatically heating hot water cylinder when temp is lo

Post by BillM »

This describes exactly what I've seen my Evohome system doing. During a very cold January the boiler would start up and open the hot water valve for 30 minutes or so, bringing the tank up to maybe 25C or thereabouts, well below its set point. Now that the temperature is well above zero this behaviour has stopped. Looks like there is an undocumented frost / freeze protect feature in the Evohome software. If so, it's fine, no problem.

Anyone seen any reference to this in the (cryptic) instructions?
armalites
Posts: 3
Joined: Wed Mar 10, 2021 4:32 pm

Re: Automatically heating hot water cylinder when temp is lo

Post by armalites »

I leave my hot water on during the day.The reality is the boiler will only fire when it needs to.It rarely fires up during the day. I have hot water priority enabled so when everyone starts having showers it keeps the water at a usable temperature.