Adding Hr92 to system

Posted: Wed Feb 28, 2018 4:08 pm
by dogman4505
Hi
had evohome controling heating for some years with evohome controller running heating as one zone. Recently added HR92 to bed rad and followed instructions to create two zones. All looked ok binding etc but realised the HR92 was not firing the boiler only the controler (lounge zone). Did some re binding and looked at instructions again and now i've ended up with it the other way around, only the bedroom will fire the boiler when adjusted, the controller is not responding when temp is adjusted.
I can't seem to see what i;ve done wrong or find what the settings should be on the controller, in the settings i've got the following
Zone name Lounge
Aplication Radiator valve
Sensor evotouch's own sensor
Zone name Bedroom
Application Radiator valve
Sensor Remote RF devices sensor
any advice would be welcome.

Re: Adding Hr92 to system

Posted: Thu Mar 08, 2018 2:45 pm
by Bart
Do you actually have radiator valves in the lounge zone?

Re: Adding Hr92 to system

Posted: Sat Mar 10, 2018 11:19 am
by Richard
As Bart has said, you would need a HR92 in the lounge zone too to have any chance of this basic level of a system operating...