Min run time & cycle rate

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
JAtherton
Posts: 2
Joined: Mon Feb 12, 2018 12:39 pm

Min run time & cycle rate

Post by JAtherton »

Hi

Just installed my Evohome, and working well.

I see in the Evohome instructions that the "min run time" and "cycle rate" defaults to I minute and 6 cycles per hour. This is said to be ideal for a gas boiler. However I have an OIL boiler (Camray 5). There is also no guidance in the boiler manual as to recommended min run time and cycle rate. Does anyone know what settings I should be using with this oil boiler?
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Min run time & cycle rate

Post by Richard »

The evohome manual doesn't explain these functions, however the Honeywell manuals of old did! 8-)

If you have a look at the old Honeywell CM900 series manual, there is an overview of cycle rate and min run time on page 8 - http://www.honeywelluk.com/Documents/In ... f/1069.pdf

So for oil boilers Honeywell TPI control should be set to 3 cycles per hour and minimum on time of 4 minutes... 8-)
Attachments
CM921-Installation-Guide (1).jpg
CM921-Installation-Guide (1).jpg (175.16 KiB) Viewed 387 times
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
JAtherton
Posts: 2
Joined: Mon Feb 12, 2018 12:39 pm

Re: Min run time & cycle rate

Post by JAtherton »

That's great, thanks for your help.