HR92 - "Valve E2" Message

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
edteamslr
Posts: 4
Joined: Fri Sep 29, 2017 10:44 am

HR92 - "Valve E2" Message

Post by edteamslr »

Hi,

One of the valves that arrived only reverts to a message of "E2 VALVE" when left for a while. I have bound it to zone before I fitted it to the radiator and it is appears to be correctly showing other data items on the screen.

What does this error mean and will it necessitate and return?
edteamslr
Posts: 4
Joined: Fri Sep 29, 2017 10:44 am

Re: HR92 - "Valve E2" Message

Post by edteamslr »

The message doesn't stop appearing after installed on the radiator but the temp display appears to work. I don't recall hearing the motor actuate at all but I could be wrong. I have a load of other ones and they don't do this.

Image
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: HR92 - "Valve E2" Message

Post by Richard »

Take the valve base plate out of the HR92 and then lock the locking catch. When the CYCL shows on the screen, is the black gear cog inside the HR92 rotating? If so the valve base plate is broken, if not the HR92 is broken. Either way, give us a call and we will resolve for you. 8-)
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
edteamslr
Posts: 4
Joined: Fri Sep 29, 2017 10:44 am

Re: HR92 - "Valve E2" Message

Post by edteamslr »

Hi,
Quick reply! Instructions followed. The black cog does not rotate. When I shut the locking catch and waited, the CYCL did not show. I tried binding it to a fake zone because I remember the others did CYCL when I was setting them up. it showed SYNC briefly but it now makes sense that I haven't ever heard the motor/gears working on this one.