Evo as hall sensor with HR92 in other rooms

Posted: Thu Jul 21, 2016 8:15 pm
by SplanK
Hi
I am sure I read somewhere the other day that it was advised unless you are using the Evo home controller (mk3) in a single zone configuration, you should avoid using the built in temp sensor to call for heat?

I have a combi boiler fitted with the BDR91 relay, and the Evohome controller is fitted in the hall (direct replacement for old stat).

I presently do not plan to fit a HR92 to the hall rad but I would like a way to control rads that I plan to keep as manual valves, or rads that I have yet to fit a HR92 to (12 so will be buying 4 packs when funds/wife allows)

Once I have started fitting HR92's and configured into zones, is it still possible to call for heat from the main controller itself in the 'Hall' zone?

Thanks

Re: Evo as hall sensor with HR92 in other rooms

Posted: Fri Jul 22, 2016 8:40 am
by Richard
The configuration you want is not possible.

Once you have gone down the 'multi zone' route with HR92's in a situation like a combi boiler, any zone you want to control must be done with a HR92 on the radiator (even if you then use an external sensor such as the evohome Controller for that zone).

Rooms/zones that have no HR92 control will come on and off with another HR92 controlled zone.

Re: Evo as hall sensor with HR92 in other rooms

Posted: Fri Jul 22, 2016 9:34 am
by SplanK
A touch annoying but not the end of the world I suppose. I guess this has saved me a whole load of grief when it comes to setting it up in multi zone so there is that :)

Will probably fit a HR92 to the hall rad in that case so its 'compliant' with the multi zone requirement of evo, and my requirement for a "hall/core" zone.

Thanks for your guidance.