x-plan and ABV
I've always wondered if a system that is x-plan needs an automatic bypass? As there is always a path through the pipework, even if all TRVs have closed, what benefit does a ABV give?
Re: x-plan and ABV
X Plan doesn't require an ABV, but that is assuming you do have an open radiator (normally we don't control the towel rads when fitted). If you do have TRV's on all rads, and they are all closed, if the central heating water cannot flow around the system, what stops the boiler overheating? You will find most boiler manufacturers require a minimum flow rate through the boiler heat exchanger, and this is what the ABV is for.
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
Re: x-plan and ABV
Surely the water still flows if all radiators are shutdown, it just flows around the pipes. Or are you saying the flow rate is too low.
Re: x-plan and ABV
Heating systems don't work like this. They are piped in parallel so no flow through TRV's = no flow at all.lloyd wrote:Surely the water still flows if all radiators are shutdown, it just flows around the pipes. Or are you saying the flow rate is too low.