Adding boiler control

Post by Tregrill »

My Evohome setup is an S Plan system with Hot Water.
So 3 zone valves each operated by a wireless thermostat via relay boxes and the Controller.
No individual wireless TRVs, they didn't work reliably in our old stone building.

Is it possible to add a boiler relay to control it and would that offer any benefit in energy reduction?
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Adding boiler control

Post by Richard »

Yes you would gain some benefit, as the BDR91 acting as the boiler relay would look at all the demands on the evohome system and operate the boiler accordingly. Important to disconnect the switch lives from the zone valves then though, as you don't want double demands, if you know what I mean.
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
Tregrill
Posts: 8
Joined: Sat Jan 06, 2018 6:51 pm

Re: Adding boiler control

Post by Tregrill »

Thanks for the reply, yes I understand the 'duplication' comment.
Is there a wiring schematic for this kind of setup, or even a description of what does what when and why?

Looking and listening to my current setup the boiler fires every 20 mins, presumably because of the Evo's 3 cycles/h setting, but it appears to do this even when there is no Room Sensor demand?
That seems odd and on mild days wasteful.
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: Adding boiler control

Post by Richard »

Tregrill wrote:Thanks for the reply, yes I understand the 'duplication' comment.
Is there a wiring schematic for this kind of setup, or even a description of what does what when and why?

Looking and listening to my current setup the boiler fires every 20 mins, presumably because of the Evo's 3 cycles/h setting, but it appears to do this even when there is no Room Sensor demand?
That seems odd and on mild days wasteful.
evohome works on 4 minute RF cycle windows. Sounds like you might have some RF comms issues going on.