HR92 often opens only for a few percent, boiler doesn't fire

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
BrechtM
Posts: 3
Joined: Thu Sep 22, 2022 10:49 am

HR92 often opens only for a few percent, boiler doesn't fire

Post by BrechtM »

Hi everyone,
I'm encountering an issue with one of your HR92's. When changing the setpoint to a higher temperature, the valve opens but often only for a very small amount (02 - 07 percent). It stays like this for hours. In those cases, it does not trigger heating demand.
On other times, it opens to 100% and triggers heating demand.

I'm wondering if this is still some learning phase as I installed them a couple of weeks ago. However, I don't understand why it would open for only a couple of percents and not trigger the boiler. Not much to learn in that case...

I have replaced batteries, re-paired and reseated the TVR with the valve fully opened (CYCL runs fine after installing TVR)

Thanks
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: HR92 often opens only for a few percent, boiler doesn't

Post by Richard »

What valve bodies are they fitted to?
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
screamagain
Posts: 4
Joined: Sun Nov 13, 2022 10:53 am

Re: HR92 often opens only for a few percent, boiler doesn't

Post by screamagain »

Hi BrechtM

I have the same issue.

So should an HR92 be fitted to a specific valve body? If so I’m going to buy 8 and sort this once and for all.

Glad you raised the topic.

Stephen
The Heating Consultant
Posts: 5
Joined: Wed Nov 16, 2022 9:03 am

Re: HR92 often opens only for a few percent, boiler doesn't

Post by The Heating Consultant »

Some radiator valves have a rubber plunger on the valve actuator and this compresses. This means the HR91/HR92 can open 10-15% and still there is no flow through the radiator valve. Higher quality radiator valves don't have this issue. If the radiators valves are old, I would also consider changing them out if you have this issue.
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: HR92 often opens only for a few percent, boiler doesn't

Post by Richard »

Our advice is to change any radiator valves that are over 15 years old. We sell Honeywell valves here - https://thesmartthermostatshop.co.uk/pr ... well-home/

Alternatively we sell IMI Eclipse valves which have patented pressure independent technology, and guarantee the correct flow rate goes through each radiator once they are set (saves hours trying to balance heating systems correctly) - https://mwphs.co.uk/product/imi-eclipse ... 690-61800/
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)