With evohome we can setup a BDR91 as a 'heating valve actuator' which can be linked to the secondary pump.thecarfixer wrote:Thanks, that makes sense.
And in terms of controls; I’m thinking through - how would the secondary pump be activated when using an opentherm gateway? I know I’d drive the UFH pump from the HCC80 pump output, but not sure how to drive the rads secondary pump when any radiator is calling for heat?
[edit] doing some reading and thinking; I am guessing what I use is the opentherm gateway on the boiler, then a BDR91 run in a zone valve configuration to open a valve and run the pump from the switch contacts in the valve?
Intergas Xtreme combi with rads, UFH and evohome Opentherm
Re: Intergas Xtreme combi with rads, UFH and evohome Openthe
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home