Mrbigfeet
Posts: 1
Joined: Sat Oct 26, 2019 3:15 pm

BDR91 comms errors

Post by Mrbigfeet »

I regularly get displayed "comms fault, boiler relay".I clear the error and all is well.
However when I looked at the Fault Logbook, this fault is recorded every day at 13.09.
Well, the last two days it was 13.09 but the eight days prior was at 13.08 and the two days prior
To that was 13.07 and the previous day was 13.06. Obviously something is happening about that time every day but
I don't know what. It does not coincide with any switch point.
Any ideas would be greatly appreciated.
gemset
Posts: 3
Joined: Thu Dec 19, 2019 8:36 pm

Re: BDR91 comms errors

Post by gemset »

Mrbigfeet wrote:I regularly get displayed "comms fault, boiler relay".I clear the error and all is well.
However when I looked at the Fault Logbook, this fault is recorded every day at 13.09.
Well, the last two days it was 13.09 but the eight days prior was at 13.08 and the two days prior
To that was 13.07 and the previous day was 13.06. Obviously something is happening about that time every day but
I don't know what. It does not coincide with any switch point.
Any ideas would be greatly appreciated.
Did you solve this problem because I'm getting the same error at 19:18 every day?
Beardaly
Posts: 2
Joined: Wed Jul 15, 2020 9:08 am

Re: BDR91 comms errors

Post by Beardaly »

Same here, pulling my hair out trying to solve this problem. Any help would be greatly appreciated.
Mower world
Posts: 2
Joined: Thu Jul 16, 2020 7:32 pm

Re: BDR91 comms errors

Post by Mower world »

My bdr91 binds up and then starts to flash red slowly but when the hot water comes on so is the heating and I have charged nothing in the year I have fitted it.
The system must have a bug or something?
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: BDR91 comms errors

Post by Richard »

There is no 'bug' and installation images always help where you have specific problems. :geek:

These errors are normally caused because you have bound the evohome system a certain way and haven't removed the existing bindings. So for instance, if you have setup the evohome Controller on an S Plan system using one BDR91 to control the heating motorised zone valve and one BDR91 to control the hot water BDR91, you don't have a 'wireless relay box' for your boiler control. Therefore if you are getting a 'comms fault, boiler relay' error, you need to tell the evohome Controller you don't have one by removing it from the BOILER CONTROL menu (select 'NONE') under SYSTEM DEVICES in the INSTALLATION MENU. 8-)
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: BDR91 comms errors

Post by Richard »

Just to add, this is an image we had from a customer with evohome 'issues'. :oops:

The CS92A and BDR91's are too close to each other. This will cause signal issues, as all the evohome devices transmit at the same time to the evotouch controller. If your systems have been installed in a similar way, this can be a cause of BDR91's with red lights on them. :geek:
evohome_bdr91_and_cs92a_incorrect_1.jpg
evohome_bdr91_and_cs92a_incorrect_1.jpg (392.51 KiB) Viewed 607 times
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
Beardaly
Posts: 2
Joined: Wed Jul 15, 2020 9:08 am

Re: BDR91 comms errors

Post by Beardaly »

Many thanks. Will start setup again with newly gained knowledge ;)