kenm
Posts: 9
Joined: Tue Nov 29, 2016 1:10 pm

HR92 on return

Post by kenm »

Hi,

A new radiator was installed with the TRV on the return pipe and not on the flow.
Does it matter if the HR92 is placed on the return and not the flow? Will this impact the performance of the radiator/system, or cause any other issues?

Thanks,
KEn
Paul
Posts: 6
Joined: Sun Oct 29, 2017 8:54 pm

Re: HR92 on return

Post by Paul »

Providing the valve body can be used in either direction (Which most can these days) then the HR92 will work perfectly, I have a few on the return flow, at the end of the day the HR92 is responding to the room temperature and just closes any valve it is attached to.

Paul
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: HR92 on return

Post by Richard »

kenm wrote:Hi,

A new radiator was installed with the TRV on the return pipe and not on the flow.
Does it matter if the HR92 is placed on the return and not the flow? Will this impact the performance of the radiator/system, or cause any other issues?

Thanks,
KEn
All depends on the Delta P of the heating system... If you have high pump pressure from a fixed speed pump and all the HR92's are closed without a suitable automatic bypass valve, then that last valve fitted on the return with its valve seat in the same direction of flow could cause 'water hammer' where the valve seat bounces on the valve body. Not so common these days with boilers and systems with modulating pumps, but in the early days of fitting evohome this was a common problem.