All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
richardgarbett
Posts: 1
Joined: Mon Aug 06, 2018 2:57 pm

2 boiler set up with hw

Post by richardgarbett »

I have an oil sytem with 2 boilers for heating they are controled by 2 controlers 1 upstairs 1 downstairs the heating works fine each controler can switch on both boilers for heat what i want to do is with the upstairs controler only swith on 1 boiler when HW is required not both at the moment HW switches on both boilers is there a way of doing it.
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: 2 boiler set up with hw

Post by Richard »

You would have to setup each controller as 'zone valve' zones and have hot water on one of them setup as hot water only. You may have to use relay's to prevent a back feed to the second boiler when you are calling for hot water demand on the individual boiler.