BDR91 / Y87RF - actuator on above target temperature

All Honeywell Home evohome general discussion in here! *PLEASE NOTE* Official Resideo technical support is on 0300 130 1299.
Post Reply
jrhartley
Posts: 3
Joined: Mon Feb 26, 2018 9:45 pm

BDR91 / Y87RF - actuator on above target temperature

Post by jrhartley »

Hello,

We have a multi-zone evohome set up which has been working fine for the past couple of years. Until this weekend, when I noticed that zone controlling radiators (other zones are UFCH zones) was on despite the evohome controller showing the temperature on the Y87RF room stats was greater than the target temperature. The evohome controller seems to be recording the correct temperature wirelessly from the various Y87RF room stats, but despite the room stat temperature exceeding the target temperature for that zone, the green light is showing on the BDR91 and the boiler is firing non-stop.

If anyone has any suggestions on how to get the BDR91 to follow the programmed temperatures that information would be much appreciated.
User avatar
Richard
Site Admin
Posts: 1199
Joined: Fri Jun 10, 2016 4:08 pm
Location: Mid Wales
Contact:

Re: BDR91 / Y87RF - actuator on above target temperature

Post by Richard »

How much above set temp are we talking?

The 'control bandwidth' which is used to accurately control the air temperature in the room factory set at 1.5 degrees C either side of setpoint for TPI control (BDR91 wireless relay box) and 1 degrees C for OpenTherm control (R8810 OpenTherm Bridge).

So for a BDR91 controlled system, the thermostat temp could be 1.5 degrees over the setpoint before the relay will be 100% off. Remember the system isn't trying to get the room up to temp and then shut off, it is trying to maintain your setpoint.

If you are fully aware of the information I have given and this is something new or odd, try turning the BDR91 off from the main power supply for a few minutes and then back on... This may cure your problem. 8-)
Home: 2012 Built Oak & Timber Frame Home (EPC Score 95 - A Rated)
Renewable Tech: GSHP, Solar Thermal, Solar PV & 20kWh Battery Storage
Smart Home Platform: Home Assistant, Shelly & Salus Smart Home
jrhartley
Posts: 3
Joined: Mon Feb 26, 2018 9:45 pm

Re: BDR91 / Y87RF - actuator on above target temperature

Post by jrhartley »

Thanks for your reply. A good 3 or 4'c. We had our boiler serviced today and I mentioned it to the engineer - I think he wiped & rebound the wireless stat to the relay and it seems to have reverted to normal now. Not sure what that happened but at least it's fixed now.

Thanks again for your help.
Post Reply