Search found 4 matches

by beefcurtains1977
Mon Nov 28, 2016 9:11 pm
Forum: Honeywell Home evohome
Topic: New installation
Replies: 4
Views: 352

Re: New installation

Any thoughts on how to clear the comms fault, if i make a change on the rad valve with the comms fault it is shown on the controller so it must be communicating.
by beefcurtains1977
Mon Nov 28, 2016 6:15 pm
Forum: Honeywell Home evohome
Topic: New installation
Replies: 4
Views: 352

Re: New installation

Thanks, from what i can see its wired properly.

I will check out the binding of the controllers for heating and DHW rather than the boiler itself.
by beefcurtains1977
Sat Nov 26, 2016 5:28 pm
Forum: Honeywell Home evohome
Topic: New installation
Replies: 4
Views: 352

Re: New installation

When the hot water reaches temperature the relay for the hot water switches off but so does the heating from what i can see, the Heating relay is still on but there is no circulation noise coming from the system and the boiler is not firing. |There are still zones calling for heat.
by beefcurtains1977
Sat Nov 26, 2016 4:49 pm
Forum: Honeywell Home evohome
Topic: New installation
Replies: 4
Views: 352

New installation

Hi Guys New user with a few questions! I have a Y-plan heating system and the heating only seems to come on when the DHW is on. I have the Hot water kit installed, 2 wireless relays for the boiler and stored hot water and 5 HS92 rad valves (one on every rad in the house). Manually overriding the set...